Which type of surges does a plug-in protector address? A type surge that typically does no damage.
Complete nonsense.
A type that is typically made irrelevant by protection already inside appliances.
Also complete nonsense.
Earth a 'whole house' protector for over 99.5% of protection (a number from the IEEE). And then add plug-in protectors for maybe another 0.2% protection.
Repeating:
The 99+% figures are from the IEEE "Green" book. They are for lighting rods. The have nothing to do with surge protectors.
For typically destructive surges, a protector either connects to earth ground. Or does not claim to protect from that type of surge.
Repeating:
Complete nonsense. Some even have protected equipment warranties.
If that was incorrect, then you posted the manufacturer spec number that says otherwise. No spec numbers posted because those type protectors do not such protection.
Complete nonsense.
Spec numbers were provided including by Nuke61 (and then referenced by westom).
NIST Page 42 figure 8 clearly demonstrates what happens when the protector is too close to appliances and too far from earth ground. A nearby TV is damaged by 8000 volts (their number). Because the best connection from protector to earth was destructively via that TV - 8000 volts.
Anyone with minimal mental abilities can discover what the IEEE surge guide says in this example:
- A plug-in protector protects the TV connected to it.
- "To protect TV2, a second multiport protector located at TV2 is required."
- The illustration "shows a very common improper use of multiport protectors"
- In the example a surge comes in on a cable service with the ground wire from cable entry ground block to the earthing system at the power service that is far too long. In that case the IEEE surge guide says "the only effective way of protecting the equipment is to use a multiport [plug-in] protector."
- westom's favored power service protector would provide absolutely NO protection.
Where is effective protection? Missing because a 'whole house' protector was not properly earthed.
In the example above a 'whole house' protector would have provided no protection. The surge was not coming in on power service wires.
Repeating:
Service panel protectors are a real good idea.
But from the NIST guide:
"Q - Will a surge protector installed at the service entrance be sufficient for the whole house?
A - There are two answers to than question: Yes for one-link appliances [electronic equipment], No for two-link appliances [equipment connected to power AND phone or cable or....]. Since most homes today have some kind of two-link appliances, the prudent answer to the question would be NO - but that does not mean that a surge protector installed at the service entrance is useless."
This is an example of a "two-link appliance."
Every responsible or professional organization describes protectors that protect from ALL types of surges.
They certainly do.
Both the IEEE and NIST include plug-in protectors as effective surge protectors.
A properly earthed 'whole house' protector means no plug-in protectors are necessary.
A 'whole house' protector would have provided NO protection in the example westom cited above.
In that example the IEEE says "the only effective way of protecting the equipment is to use a multiport [plug-in] protector."
And repeating:
SquareD says for their "best" service panel protector "electronic equipment may need additional protection by installing plug-in [protectors] at the point of use."
1000 joules means it only protects using 333 joules and never more than 667 joules. And does nothing to protect from destructive surges - typically hundreds of thousands of joules.
Repeating:
As I wrote in my first post, the author of the NIST surge guide looked at the amount of energy that could make it to a plug-in protector. Branch circuits were 10m and longer. The surges coming in on power wires were up to 10,000A. That is the maximum that has any reasonable probability of occurring, and is referenced in the IEEE surge guide. The maximum energy at a plug-in protector was a surprisingly small 35 joules. In 13 of 15 cases it was 1 joule or less.
I then explained why the energies at a plug-in protector are so low. All ignored by westom.
1000J, or 333J, are far higher than the 35J that is the maximum that has any reasonable probability of reaching a plug-in protector. A plug-in protector with high ratings (like 1000J), properly connected (as in my first post) is very likely to protect from a very near very strong lighting strike. That is one of the reasons manufacturers can have protected equipment warrantees.
The effective protector is typically 50,000 amps. That Square D protector I believe is only 22,000 amps. Two are recommended to earth and remain functional. So that even a direct strike to the telephone pole causes no household damage.
The author of the NIST surge guide also looked at the surge current that might come in on power wires. The maximum with any reasonable probability was 10,000A per wire (as stated above). That is based on a 100,000A lightning strike to a utility pole adjacent to the house in typical urban overhead distribution. Only 5% of strikes are stronger, and the strike is extremely close.
A properly sized protector at the service panel is very likely to protect from very near very strong lightning strikes. Recommended ratings are in the IEEE surge guide on page 18.
Still missing - any source that agrees with westom that plug-in protectors do NOT work.
For real science read the IEEE and NIST surge guides. Excellent information. And both say plug-in protectors are effective.