I cant take any chances as long as there are conflicting accounts, because it seems like APC changes things around. From their knowledgebase:
It doesnt even explain what the difference is between later and earlier SUA models, so for all I know, that model may very well have the fan on 100% of the time. The fact that the fan is always on at 75% load and greater is also a bit of a turn off, since I'm still not entirely sure how much I'm going to be asking of my UPS.
A fan is included on any Smart-UPS 1400 VA higher and on all "XL" models.
All "SU" model units and earlier "SUA " units utilize a single speed fan. The fan will only be on during the following scenarios:
1. The UPS is on battery.
2. The UPS is charging the battery.
3. The UPS has a load greater than 75%.
4. The internal temperature of the UPS has reached greater than 140 degrees F (60 degrees C). Note, for 4th Generation units (model number begins with SUA) the temperature range has changed. For these models, the internal temperature will have to be greater than 104 degrees F (40 degrees C)
Later SUA model units utilize a 2 Speed fan. On these units the fan will always be on in low speed mode, and will switch to high speed mode should one of the following events occur:
1. The UPS is on battery.
2. The UPS is charging the battery.
3. The UPS has a load greater than 75%.
4. The internal temperature of the UPS has reached greater than 104 degrees F (40 degrees C).
It doesnt even explain what the difference is between later and earlier SUA models, so for all I know, that model may very well have the fan on 100% of the time. The fact that the fan is always on at 75% load and greater is also a bit of a turn off, since I'm still not entirely sure how much I'm going to be asking of my UPS.